Re: Solar Energy, A Complement To FTA by pdozie: 1:41pm On Jan 23, 2016 |
kiekie1: Sent you both PM and SMS yet no replies ![]() Need info on Trojan batteries and other items - patdozie@yahoo. com |
Re: Solar Energy, A Complement To FTA by chris81964(m): 3:18pm On Jan 23, 2016 |
zeestone99: Check again |
Re: Solar Energy, A Complement To FTA by kiekie1(m): 4:30pm On Jan 23, 2016 |
pdozie: Am sorry , I have been busy Sir... Will call you asap! Thanks |
Re: Solar Energy, A Complement To FTA by kiekie1(m): 6:30am On Jan 24, 2016 |
HURRY ! HURRY !! DISCOUNT SALES !!!!!! TROJAN IND 17-6V industrial line flooded lead acid batteries (1202AH) ......@ 340k USA TROJAN L16-RE Premium Line Flooded Lead Acid Battery 6V (410AH)20hr Rate *NOW IN STOCK*..... @ 87k USA TROJAN J185P-AC Signature Line Flooded Lead-Acid Battery 12V (205AH) 20hr Rate .... "NOW IN STOCK"....@75k Solarworld mono panels 255w ,260w,265w "made in Germany" etc now in stock at very discounted prices......... YACHI SOLAR PANELS: 130w mono........ 30000 200w mono........ 45000 250w mono........ 55000 300w mono........ 62000 PERLIGHT SOLAR MODULES POLY SOLAR PANEL: 80W N14000. 100W N16000. 120W N20000. 200W N40000. 240W N45000. 300W N50000 MONO SOLAR PANEL: 80W N12000. 100W N15000. 110W N15500. 120W N18000. 130W 20000.180W N28000. "OUT OF STOCK" Latest model 10kva wall mount servo stab (AC input range 80V-270V)....... @55k Must power star light inverters with charge current adjustable variable,LCD display,wall mount,remote port,load wattage display,flooded/gel/agm battery settings,battery equalisation and desulphation settings... 1kw 12v =60k 1.5kw 12v =70k 2kw 12v =85k 2kw 24v =85k 3kw"4kva" 24v =140k 4kw 24v/48v =160k 5kw 24v/48v =180k 6kw"7.5kva"24/48v=220k 8kw 192v. =350k 10kw 96v. =380k Programmable timer switch with LCD display 220vac 16a........ @5k Infinitum battery desulphators 12v & 24v "NOW IN STOCK" New Epsolar Tracer A series available.30a 12-24v auto select. . Max pv input voltage 100v. It has excellent features like: -inbuilt LCD display, -high efficiency energy harvest with advanced mppt algorithm -dual core (ARM CPU+DSP) control architecture -run data and event recording -multi phase synchronous rectification tech realizing peak conversion efficiency 98% -high reliabilty including reverse connection, over current and load short protection etc -diversified load control mode -monitor software supplement and firmware update -extensive communication capabilities (RS232, RS485 with modbus protocol, CAN bus extendable)....@50k Mercury tubular/flooded12v 220a batteries "18 months warranty" @ 55k Mercury deep cycle 12v 200a batteries @ 55k GP Malaysian deep cycle 12v 200a batteries @ 60k 10mm² black armoured solar panel-charge controller cables with earth/grounding flex "silver copper based & heat resistant " ... @ N1000 per yard CSUN panels arriving soon..... *AUTHORISED DEALER PRAGMATIC TECHNOLOGIES* All our prag / cyberpower products comes with reliable warranty *AUTHORIZED DEALER SOLAR SHOP LTD PRODUCTS* All our products come with 1 year Warranty For best affordable prices,contact Smartcell Global Services,Lagos Nigeria. Simply call Sir Frankie "08135031951" for purchase,fast delivery and waybills .. Thanks !! |
Re: Solar Energy, A Complement To FTA by zeestone99(m): 12:08pm On Jan 26, 2016 |
Call us for durable and affordable inverters and solar panels, we install nationwide. Standard battery and solar rack mount also available. You can reach us on 08117398294, or email Info@monzpowersolutions.com |
Re: Solar Energy, A Complement To FTA by durodee(m): 6:31pm On Jan 26, 2016 |
Battery Desulfation Find out how to desulfate/desulphate and rejuvenate lead acid batteries home > storage | electronics Printer Friendly Version Print Article Lead plates in a lead acid battery - battery desulfation A Lead Acid Battery is made up of plates of lead in a case filled with an electrolyte (dilute sulphuric acid). When the battery discharges, some of the lead from the plates combines with the electrolyte to make lead sulfate (PbSO4) which builds up on the surface of the plates as crystals (as electrons leave the battery as electricity). This is called sulfation. When the battery is next charged this process is reversed with the lead sulfate crystals breaking down - returning the lead to the plates and restoring the electrolyte to its original composition. BUT, each time a battery goes through this discharge/charge cycle some of the lead sulfate crystals remain and over time harden, thicken, and grow over the surface of the lead plates. This is a particular problem when batteries are left discharged for long periods of time and when they are deeply discharged. Lead sulfate on the plates of a battery acts like an insulator reducing the plate area in contact with electrolyte. Over time this build up of lead sulfate crystals will result in a battery which cannot hold much charge - i.e. effectively a dead battery which needs to be replaced. Reconditioning a Lead Acid Battery Desulfation (also know as Reconditioning or electrolyte stratification) offers a way for dead batteries to be brought back to life and for tired batteries to be rejuvenated. It can also be used every few months to keep batteries in the best possible condition all the time. Desulfation will not bring batteries with a shorted cell or worn out plates back to their former glory, but it is a valuable tool for anyone depending on battery storage for power who cannot afford to buy new batteries. When lead sulphate crystals build up on the lead plates, it is not an easy task to remove them and thereby recondition the battery. Breaking down hardened crystal build up and dissolving cystals back into the electrolyte requires a charging voltage much higher than would ever be used to actually charge the battery. But, if you were to put this constant high voltage through the battery it would overheat, release gas, and could potentially explode. Therefore pulse conditioning is used to give very short blasts of high voltage sufficient to shift the lead sulphate crystals without overly raising the temperature of the battery as a whole. Desulfation pulses shown on a scope Every lead acid battery has a resonant frequency at around 2 to 6 megahertz. If pulses of electricity (high frequency, high voltage, but low power) are sent into the battery, rhythmic beating (resonance) of the plates causes the crystalline deposits to break up and the sulphate returns to the electrolyte solution. This process takes three to four weeks typically during which time the battery must be trickle charged (in parallel with the desulphator) so that the battery ends up reconditioned and fully charged. Below is a video showing the lead plates inside two identical batteries - one which has been desulphating for three weeks, and one which has been left in its original sulfated condition. Note that the voltage measured across the battery terminals will drop as the desulphation takes place as the internal resistance of the cells is reduced by the clearing of the crystals on the lead plates. At the same time, the amount of charge that the battery can hold will be increasing. Build a Battery Desulfator Circuit diagram for a low power 12V lead acid battery desulfator A DIY battery desulfator circuit originally published in the US-based Home Power magazine has been successfully made for many years all over the world. Here are links to the instructions to build the Low Power (circuit design above, and finished example circuit pictured below) and the High Power versions of the circuit. These links are to be found together with a lot of other useful information here. (http://www.reuk.co.uk/Battery-Desulfation.htm) 1 Like |
Re: Solar Energy, A Complement To FTA by durodee(m): 6:34pm On Jan 26, 2016 |
Tech gurus should visit the site and mass produce for us in Naija now! |
Re: Solar Energy, A Complement To FTA by bobojoshua(m): 6:52pm On Jan 26, 2016 |
durodee: |
Re: Solar Energy, A Complement To FTA by kiekie1(m): 6:59pm On Jan 26, 2016 |
durodee: Infinitum battery desulphators are available in 12v & 24v . affordable and efficient ! Thanks Sir |
Re: Solar Energy, A Complement To FTA by bobojoshua(m): 10:46pm On Jan 26, 2016 |
JUO: |
Re: Solar Energy, A Complement To FTA by hisenjos: 1:53am On Jan 27, 2016 |
Update 4 months and counting. Still waiting for a refund. 16m plus of business and get treated this way? Still dumbfounded and shaking my head. See last communication with Richmond. hisenjos: 1 Like
|
Re: Solar Energy, A Complement To FTA by tivta(m): 8:29am On Jan 27, 2016 |
hisenjos: What I have noticed about Nigerian businesses is that most business people HATE making refunds, they will always bring up one issue or another, it is always best to plan ahead before doing business, this is another reason why I hate paying by instalment. It is even written in most receipt "goods sold are not refundable" Richmond seems willing to pay back, you just have to be patient, hope you have learnt not to ask for refunds and plan ahead before buying anything in this country. Good luck. 2 Likes 1 Share |
Re: Solar Energy, A Complement To FTA by bigrovar(m): 8:39am On Jan 27, 2016 |
JUO: Ideally a solar panel should not be static, It should be adjusted every month to keep it aligned with the shift in the sunrise sunset path. It is known that the sun rises from the east and sets in the west. However it does this in a 180 degree arc and if you are in the northern hemisphere (like Nigeria) you panels should be south facing (especially if it is a fixed panel without sun tracking capabilities). Now the tilt of the panel will depend on the path the sun takes when going from east to west. This path changes every month requiring that the tilt of a panel be adjusted to the full path. http://solarelectricityhandbook.com/solar-angle-calculator.html helps to calculate the required tilt of a panel based on your location month over month for optimum yield. In my case, since I do not have a month whose tilt can be adjusted month over month. I used the site to calculate the optimum tilt angle for a fixed non adjustable solar mount. For me in Abuja that was 81 degree. You can find out which one is applicable to your location. 1 Like |
Re: Solar Energy, A Complement To FTA by netotse(m): 7:29pm On Jan 27, 2016 |
My Chairmen...maximum hailings, I need a bit of advice, I am thinking of getting an inverter in the next couple of weeks, something in the range of 3-4KW, solar panels might come later. I'm worried about the inability of most of the chargers in the market to charge the batteries properly(float charge vs bulk charge), apart from the high end inverters, is there any other solution anyone can recommend? Does it make sense to connect a charge controller (without the solar panels) just to make sure the inverter batteries are charged properly? I will want to get at least 400AH of power and it would be a waste if the inverter can't charge the batteries properly. |
Re: Solar Energy, A Complement To FTA by pdozie: 9:11pm On Jan 27, 2016 |
My Learned people, please help me out with this (CC: Chris, Saipro, Abinafu, Rich etc) My 2.5KW panels runs off a 45A controller. With a 2x5 configuration (2 in series and five parallel strings). Each Panel has approx of 8.6A which is 43A for the 5 strings. Rated 24v. I plan adding about 2 more panels. If I add the string to the existing ones, it will take the Current to 51.6A. That means the 45A controller will leave some juice to waste right? Option one is to upgrade to 60Amp controller Option two is to get another 45A controller, connect the new panels to it and parallel the output of the controllers Option three is to change the strings configuration 3 x 4 (3 in series & 4 parallel strings). This will maintain a current of 34.4A which the existing controller can handle. But the voltage from the 3 strings could rise as much as 123v. Option 3 is more economical but is there Any implications or trade-off in terms of efficiency? The Controller can handle max of 150v though. I saw the The following attached diagrams in the controller manual. (Battery Current Vs Array Voltage) and (Tristar MPPT 48v Efficiency). One is showing that Current to the battery starts reducing at 140v, which seems OK for my option 3. The other is showing efficiency is higher at lower voltage. Please advice
|
Re: Solar Energy, A Complement To FTA by pdozie: 9:20pm On Jan 27, 2016 |
netotse: The only alternative apart from getting a high end inverter is to get an external charger. It will only charge the batteries when you have NEPA or GEN though. Based on the free education received here, if you get a 50Amp charger, it will take 8 hours to fully charge your bank (400/50). What I do not know is if such external chargers can regulate battery charging to avoid overcharging. Meanwhile, what is your load consumption that would warrant 4KW solar panels. The experts may need that info Disclaimer: I'm not an expert!! |
Re: Solar Energy, A Complement To FTA by abunafiu(m): 10:37pm On Jan 27, 2016 |
pdozie: This particular subject have been discussed here as far back as 2013. I'll not answer ur question directly but I'll tell you what I use personally. 9 units of 120w mono panels (24v each) . I connected 3 in series to form 3 by 3 config. I have never experienced any drop in efficiency rather I observe sometimes even 120% efficiency. I have used it on 12v, 24v and 48v systems without issues. Note: my 6mm wires got hot whit 12v and 24v systems. .I use 60amps mpppt with 16 units of T105-RE trojan batteries @ 48v. |
Re: Solar Energy, A Complement To FTA by chris81964(m): 12:46am On Jan 28, 2016 |
pdozie: You have maxed out at 45 amps. 2500 / 48 = 52 Amps more than is recommended for your 45 A controller. Your 60 amp will handle 3 kw. What is the short circuit voltage of your panels? Add 20% to that number and as long as it less than 150 V you can do your wiring to match. You can go for a 60 amp and have a clean look and less complication if money is not as much a factor. For the sake of disclosure I have a client that I installed 3 kw in panels on a 24 V system. The 80 amp controller sees 80 amps regularly and the fans come on a lot. Next time I would have done two 60 amp controllers. |
Re: Solar Energy, A Complement To FTA by bigrovar(m): 7:04am On Jan 28, 2016 |
netotse: I had similar in mind when search for an inverter. I wanted something capable of intelligent charge without draining my pocket. In the end I settled for the su-kam falcon+ which is capable of different state of charge (They called it fuzzy charging) it also came with a temperature sensor for ATC (automatic tempreture compensation) Falcon + like all Su-Kam's products, uses DT-6S Six Stage Charging technology for efficient charging and longer battery life. Su-Kam is the only company in the world to use this advanced charging technology in its inverters I got it for 33k (1050VA) For your use case you might want to look at their Fusion series which should have the capacity you seek. |
Re: Solar Energy, A Complement To FTA by pdozie: 8:02am On Jan 28, 2016 |
Hi Chris, Abunafiu, Thanks for the insights. I appreciate. |
Re: Solar Energy, A Complement To FTA by chris81964(m): 12:00pm On Jan 28, 2016 |
Im2Busy2Bother: Please whatsapp me where he bought the cables +19739981590 |
Re: Solar Energy, A Complement To FTA by Optimixim(m): 4:50pm On Jan 28, 2016 |
Buy your US flooded battery at 75k each . Very rugged as trojan and hoppecke. Mind you I have worked with solarshop and other big solar companies in lagos. Kiekie1 and remond7... You know what I mean sir so kindly contact me for your US battery... 08167327440 Was doing some jobs with diamond bank and zenith recently . All tech masters are right with their deduction over how the solar system works. But here comes a talkless man optimixim from solarshop, have done projects including ghana and many other companies.
|
Re: Solar Energy, A Complement To FTA by Barezzi(m): 9:04pm On Jan 28, 2016 |
^^ My friend, u just dey throw suspect credentials everywhere! Wetin be the rating of ya wonder batteries?!! 1 Like |
Re: Solar Energy, A Complement To FTA by Saipro(m): 10:59pm On Jan 28, 2016 |
pdozie: I like the answers you have been given and everyone is right. Your controller should more frequently see in the range of 33A to 38A and occassionally, 43+A. For a 48V system, your configuration is perfect (efficiency rises as you narrow the difference between Vmp and nominal system voltage. This might however not be the case in instances of long distances from the panels to the CC (often quoted as in excess of 30m - 50m, depending on autority and other parameters). High voltage = lower transmission loss and this can often offset whatever gain you hope to achieve by using strings of 2. My system is similar to yours (250W x 9) in three strings of 3 for a nominal 48V system. It works the CC a bit more (a Midnite Classic 150) but I have no worries on the transmission efficiency over a 10m stretch using 10mm2 cables. Those are the academics of the logic. Back to the question, if your cables are the right size (10mm2 or higher), go for the 4 strings of 3. If your cables are smaller, you might want to consider 3 strings of 4. |
Re: Solar Energy, A Complement To FTA by zeestone99(m): 1:25am On Jan 29, 2016 |
netotse: I have external battery charger for sale but I believe your inverter will be able to charge your battery well except you have a large battery bank. you can call 08117398294 or email info@monzpowersolutions.com |
Re: Solar Energy, A Complement To FTA by Optimixim(m): 6:58am On Jan 29, 2016 |
12 VOLT – MULTI-PURPOSE
U.S.
Battery
Model
Amp
Hours
(20
hr.
rate)
5 hr
rate
M.C.A.
@32F
Minutes
@ 75
Amps
Minutes
@ 25
Amps Le
16 TF-
HC
120 — — — 250
9/16" (
22 NF-
HC
60 — — — 95
7/16" (
8 D-HC 240 — — — 455
3/4" (5 |
Re: Solar Energy, A Complement To FTA by kiekie1(m): 11:01am On Jan 29, 2016 |
NOW IN STOCK : A&E 2kva 24v lcd pure sine wave power inverter .. Note;Company price (55k) ... Call and get yours now @ (50k) per unit Prospective a&e clients can call now for discounts on any product of your choice. http://aedunamis.com/ *AUTHORISED DEALER A&E DUNAMIS* All our a&e products comes with 1 year reliable warranty!
|
Re: Solar Energy, A Complement To FTA by richmon74(m): 11:44am On Jan 29, 2016 |
Optimixim: Oga I suggest you do a detailed review of the battery itself and convinced us on why the battery is value for money rather than tell us your own credentials because we are not buying you but the battery. 4 Likes |
Re: Solar Energy, A Complement To FTA by kiekie1(m): 1:00pm On Jan 29, 2016 |
richmon74: Lol |
Re: Solar Energy, A Complement To FTA by netotse(m): 10:28am On Jan 30, 2016 |
bigrovar:thanks man...will check. Been a while BTW, how's things? |
Re: Solar Energy, A Complement To FTA by bobojoshua(m): 4:48pm On Jan 30, 2016 |
GeorgeD1: 2 Likes |
(1) (2) (3) ... (123) (124) (125) (126) (127) (128) (129) ... (1923) (Reply)
Free To Air Satellite Tv General Thread
Viewing this topic: 1 guest(s)
(Go Up)
Sections: politics (1) business autos (1) jobs (1) career education (1) romance computers phones travel sports fashion health religion celebs tv-movies music-radio literature webmasters programming techmarket Links: (1) (2) (3) (4) (5) (6) (7) (8) (9) (10) Nairaland - Copyright © 2005 - 2025 Oluwaseun Osewa. All rights reserved. See How To Advertise. 121 |